short circuit and let-through current

short circuit and let-through current

short circuit and let-through current

(OP)
does the NEC recognized let-through current from a fuse when calculating short circuit? if not, what section in the NEC does is this stated? thanks!

RE: short circuit and let-through current

The basic concept is that the equipment in question must have an interrupting RATING that is adequate for the short circuit current - See 110.9.

Then see 240.86 for the requirements for using a "series rating". If you as the engineer are willing to "ensure" that the downstream device will remain "passive" while the fuse does its thing, then 240.86(A) is for you. On the other hand, using a tested combination is a much more accepted approach. The old "up-over-down" method has been discredited for about 15 years, at least.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources