Expansion Tank
Expansion Tank
Dear Members,
My question is why do we need expansion tank on chilled water system? Here is the situation ……….
Ambient temperature = 40 deg. C
Chilled water temperature = 5 deg. C
Chiller Tons: 100
Thermal expansion of water is 0.00214 1/ deg. C = 0.0043 gallons per 25 deg. C
System volume = 1200 gallon
Most probably, chiller will start when outside temperature is 25 deg. C, that gives us 25 deg. C delta T. Total system water volume expansion would be 1200-gallons X 0.0043 = 5.16 gallons
This is a very small expansion compared with the size of the system. Elbows, fittings and expansion joints can handle this expansion.
Do we really need an expansion tank?
Sincerely,
Fayaz Din
Chiller Tons: 100
Sincerely,
Fayaz Din
RE: Expansion Tank
RE: Expansion Tank
in best case your safety valve will frequently leak and you would need to add make-up water permanently.
RE: Expansion Tank
RE: Expansion Tank
RE: Expansion Tank