Dear community, maybe someone could help me:
For a 75,000 barrels diesel oil storage tank with frangible roof, I'd like to clear my doubts:
1. If the roof is frangible, do I need an emergency valve (EV)? (API 2000 says "no")
2. If the tank is open to atmosphere, should I consider internal pressure 0 Kpa and vacuum 0 Kpa? (*API-650 mention 0.25kPa and 0KPa only if the tank meets appendix H)
3. Using API 2000 5th, I calculated the inbreathing and outbreathing, where can I find the OPEN VENT sizing calculation? Or how can I size it?
*4. We have other tank for gasoline storage, with IFR and supported cone roof. Is there any problem with this configuration? (IFR and supported cone roof together)
Thanks in advance,
For a 75,000 barrels diesel oil storage tank with frangible roof, I'd like to clear my doubts:
1. If the roof is frangible, do I need an emergency valve (EV)? (API 2000 says "no")
2. If the tank is open to atmosphere, should I consider internal pressure 0 Kpa and vacuum 0 Kpa? (*API-650 mention 0.25kPa and 0KPa only if the tank meets appendix H)
3. Using API 2000 5th, I calculated the inbreathing and outbreathing, where can I find the OPEN VENT sizing calculation? Or how can I size it?
*4. We have other tank for gasoline storage, with IFR and supported cone roof. Is there any problem with this configuration? (IFR and supported cone roof together)
Thanks in advance,





RE: Redundant configuration help, sizing Open Vent, etc
2) If you have Appendix H circulation vents, then yes otherwise no
3) from vendors - each has their own set of curves for their devices but first check the latest API 2000, there may be an appendix with values
Is this a floating roof tank?
RE: Redundant configuration help, sizing Open Vent, etc
I don't like designing tanks for 0 internal pressure or vacuum if that is your second question. To estimate inbreathing or outbreathing means you need a dP and that's sort of difficult when the tank is designed for 0 pressure or vacuum.
If you mean by open vent something like a gooseneck, I do it allowing for an entrance and exit loss, pipe and fitting head loss coefficients. Bird screens are common which is another pressure drop you need to allow for.
RE: Redundant configuration help, sizing Open Vent, etc
RE: Redundant configuration help, sizing Open Vent, etc
Emergency vents are cheap in my opinion compared to replacing a roof.
That's the very good point. Wouldn be better installing an EV instead of replacing the entire roof?
IFR
I can not understand how an IFR tank with venting meeting appendix H will eliminate vacuum inside the tank and a tank without IFR open to atmosphere won't.
RE: Redundant configuration help, sizing Open Vent, etc
RE: Redundant configuration help, sizing Open Vent, etc
RE: Redundant configuration help, sizing Open Vent, etc
Another thing: API-650 mentions Pfe as "internal floating roof external pressure". I'm assuming this pressure exists only if the tank doesn't have an open vent, and its value will be equal to the tank internal pressure.
RE: Redundant configuration help, sizing Open Vent, etc
API 650 Pfe is a load related to floating roof supports and connections only and does not affect nor is it related to the tank shell design. It is applied regardless of the tank vent situation. It is not really "pressure" but a uniform live load.
RE: Redundant configuration help, sizing Open Vent, etc
About Pfe,
But isn't Lf1 already specified for "Internal floating roof uniform live load" (according to 5.2.1(e))? So what's the difference between Pfe and Lf1?
Regards,
RE: Redundant configuration help, sizing Open Vent, etc
RE: Redundant configuration help, sizing Open Vent, etc
I see now, I would never imagine liquid on top of the roof. Thank you IFR. I wonder why API-650 can't be clearer about this.
Regards.
Thank you all for the responses.