heat loads.
heat loads.
(OP)
thread403-50052: Heat Load Calculation
Found this to be a good thread. I'm stuck with calculating heat load, with answer expressed in CFM. What would be the formula if I had 5,000 gal/hr of cooling water with a 10 degree delta T?
Found this to be a good thread. I'm stuck with calculating heat load, with answer expressed in CFM. What would be the formula if I had 5,000 gal/hr of cooling water with a 10 degree delta T?





RE: heat loads.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
RE: heat loads.
500*GPM*(delta-T)
To convert to air flow in CFM, you'll need to know the difference in supply air temperature and space temperature, plus the load. Not enough info given.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies