MCC bus sizing Help

MCC bus sizing Help

MCC bus sizing Help

(OP)
I have a total of 654hp motor list, largest motor 150hp. The 150hp (on a starter contactor) runs a meat grinder which will only operate continuosly for no more than 10min at a time. My estimate gives me an 800amp bus. Will this size do the trick? how do you properly calculate the proper bus size for such load?
Thanks
Sam

RE: MCC bus sizing Help

If you are in the US and subject to the NEC, 125% of the largest FLC plus total of all other FLC of motors that will potentially be running at the same time. This is actually how you would size the main conductors if it were field wiring, but there is no other rule pertaining strictly to the bus bars that allows for anything less.

430.24 Several Motors or a Motor(s) and Other Load(s).
Conductors supplying several motors, or a motor(s) and other
load(s), shall have an ampacity not less than the sum of each
of the following:
(1) 125 percent of the full-load current rating of the highest
rated motor, as determined by 430.6(A)
(2) Sum of the full-load current ratings of all the other
motors in the group, as determined by 430.6(A)
(3) 100 percent of the noncontinuous non-motor load
(4) 125 percent of the continuous non-motor load

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies

RE: MCC bus sizing Help

If you are in Canada and subject to the CEC you are probably safe with 800 Amp bus.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: MCC bus sizing Help

What voltage are you running at?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources