VFD Over Current Protection

VFD Over Current Protection

VFD Over Current Protection

(OP)
I have a C-H MCC with a section containing a 50 Amp circuit breaker and a C-H VFD dseigned to control a 25HP motor, all new, not yet powered. Turns out the device being powered has a 10HP motor. Any problems? I am thinking of NEC motor protection.

Thanks;
Steve

RE: VFD Over Current Protection

Steve
Is there a PTC sensor (thermistor) fitted to the VFD or is it relying on electronic thermal characteristics?
The issue is not just over current protection but motor thermal protection.
I would check with C-H to determine if this meets class 20 protection for the motor if using purely the electronics of the drive to protect.

RE: VFD Over Current Protection

(OP)
The motor is not fitted with temperature monitoring. I am OK with software monitoring of motor running current. I am concerned about NEC 430.52 requirements.
Thanks;
Steve

RE: VFD Over Current Protection

The VFD is going to provide all of the protection for the motor, Overload and Short Circuit, it's part of the UL listing requirements and because the VFD is in an MCC, you know that it is UL listed. So when you program the motor nameplate data, the VFD will automatically adjust its protection parameters to take care of everything DOWN STREAM of it regarding that specific motor, it doesn't matter if the motor is smaller than the VFD regardless of the size of the CB ahead of the drive (which if you think about it, is always sized for the VFD max amp rating, not the motor rating).

That said, some VFD mfrs have a restriction as to HOW MUCH smaller the motor can be, because of the resolution of the type of current sensing devices they have on the output. Some use cheaper methods than others. I have seen some that limit the motor to no less than 1/2 the rating of the drive, so in this case, 10HP is below that threshold. But it varies from mfr to mfr, A-B PowerFlex drives for instance have no such restriction, you can program a 400HP drive to protect a 1HP motor if you want to. So only C-H can answer that for you, or it will say so in the manual if you look up the programming of the motor FLA.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources