Welded Shear Studs & Composite Floor Deck
Would anybody mind sharing the general structural notes for these two items here! Our library doesn't have these notes so I want a jump start on creating a new set of notes for both.
Thanks in advance.
Thanks in advance.
RE: Welded Shear Studs & Composite Floor Deck
Merry Xmas all.
http://www.tatasteelconstruction.com/en/reference/...
Simply supported primary composite beam
Simply supported secondary composite beam
Initial Design of Composite Beams
Composite slabs for multi-storey buildings for commercial and residential use
Composite floor slab
All about Eurocodes:
http://www.DesignToEurocodes.com
1) diameter and length of headed studs required
2) general instructions of how to layout the studs in the low flutes of the deck
3) Maximum stud spacing along beam, minimum side to side spacing, clearance from edge of beam flange, additional studs, etc.
4) Fastening of deck to beams
5) Removal of ceramic ferrules
6) Restrictions on erection of masonry walls on composite slabs until proper curing.
I hope this helps....
HEADED STUDS
HEADED STUD MATERIAL TO ASTM A307 AND CSA W59, INCLUDING APPENDICES. MIN GRADE 60 KSI AND WELDABLE
HEADED STUD LENGTH IS TO U/S OF STUD HEAD
MAX HEADED STUD DIA SHALL NOT EXCEED 2-1/2 TIMES BASE MATERIAL THICKNESS
MIN STUD LENGTH TO DIA RATIO FOR HEADED STUDS SHALL BE 4
HEADED STUD SHALL PROJECT 2X STUD DIA INTO CONC OVER STEEL DECK
HEADED STUD LONGITUDINAL SPACING SHALL BE 6X STUD DIA MIN AND TRANSVERSE SPACING SHALL BE 4X STUD DIA MIN
WELD AND TEST HEADED STUDS TO CSA W59, INCLUDING APPENDICES
WELD HEADED STUDS TO STEEL SECTIONS AT LOCATIONS SPECIFIED
DECK FOR WELDING THROUGH SHALL BE 2 SHEETS MAX IN CLOSE CONTACT. THICKNESS OF EACH SHEET SHALL BE [0.060" |1.52MM] (CNT) PLUS Z275 HDG COATING
DO NOT APPLY COATING SYSTEM TO SURFACES TO RECEIVE HEADED STUDS
COMPOSITE CONSTRUCTION IS [SHORED | UNSHORED]
Modify as needed CSA W59 is a Canadian welding code...
Dik