Hydraulically most demanding area shape, regarding walls
NFPA 13 says to use 1.2 * sqrt(min remote area) to find the L dimension of the remote area rectangle. I need to know if this means we just ignore walls and assume the fire teleports through them, or if we use them as barriers and can then make square or "tall rectangle" remote areas, see the pdf for graphical representation.
RE: Hydraulically most demanding area shape, regarding walls
22.4.4.1.2 Room design method states "Where the design is based on the room design method, the calculation shall be based on the room and communicating space, if any, that is hydraulically most demanding".
In this case, you would stop at the walls. All depends on which method best suits your particular design.
Keep in mind that NFPA 13-2010 22.4.4.1.1.3 states "In systems having branch lines with an insufficient number of sprinklers to fulfill the 1.2 requirement, the design area shall be extended to include sprinklers on adjacent branch lines supplied by the same cross main." Meaning, the only time your design area is permitted to be shorter than 1.2*sqrt(DA) is when the branch lines are not physically long enough to fulfill the requirement.
Can anyone put forward a probable theory as to why it's this way, when clearly a fire is going to be hindered by a wall, especially one without a door or a CMU fire wall. NFPA, I want to understand you!
http://www.nfpa.org/categoryList.asp?categoryID=71...
I can't follow that article as I'm new to sprinkler design and haven't even seen the circa 2003 nfpa 13, and all of the sections he refers to for that quote are missing/different now in nfpa 13 2013. From what I gathered, however, he is saying to sometimes treat walls as boundaries as a safety factor, because it could cause elongated remote area shapes along branch lines and make the hazard more demanding, which is the opposite of my case. Treating walls as barriers in my case would mean more of a square shape for a remote area.