I have a question about a girder in a wood truss floor system. Can a 24" deep multiple ply girder span 25.1' and carry 1278 lb/ft?

RE: Wood Truss Girder Capacity

No way to tell without referring to the species of lumber, size of members, connection capacities at joints, etc.

If you can locate the original manufacturer they might be able to get you capacity information.

If not - then probably load testing would be the only way to know.

RE: Wood Truss Girder Capacity

That is a reverse engineering solution --- JAE has it right. MUCH more info required...

RE: Wood Truss Girder Capacity

(OP)
Sorry. This is a condition that I have on a set of drawings and the truss designer says it won't work.

RE: Wood Truss Girder Capacity

Then maybe you should beleive him unless you check it your self

RE: Wood Truss Girder Capacity

That’s a fairly substantial load for a steel beam, let alone a 24" deep wood truss. The problems will probably be duration of loading, deflection and ganging the several trusses together to actually get them to properly share that loading. Is it a one sided or two sided loading?

RE: Wood Truss Girder Capacity

(OP)
It is two sided

RE: Wood Truss Girder Capacity

How wide is the girder?
\
I see a maximum shear of 16K and a max moment of 100 Kip feet. That amopunt of moment is a lot for a wood beam, an awful lot. The shear is marginal depending on the width, and we nave not addressed deflection yet.

Right now, with no further information, I would defer to the opinion of the truss designer.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Wood Truss Girder Capacity

(OP)
He says it doesn't work with 5 ply.

RE: Wood Truss Girder Capacity

Didn't check deflection, but you can get a glulam or powerbeam to work within those dimensions for strength. Not sure if switching to glulam is an option.

RE: Wood Truss Girder Capacity

(OP)
Increased depth. Thanks for the input.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources