Redundant member in lattice towers

Redundant member in lattice towers

Redundant member in lattice towers

(OP)
Hi,

I have some doubts with the definition of redundant members.

The horizontal or the redundant members with less than 15º(or 30º, I'm not sure) sould have define with the load of a worker. Am I right? ASCE 10-97 3.14.8.

And the rest of redundant member only according KL/r with L/r<250?

Thanks.

RE: Redundant member in lattice towers

If you run the latest version (or a fairly recent version) of PLS-Tower, there is a redundant analysis check that will check for man loads and a load case that will most likely be in ASCE-10 for the next revision that will be coming out soon. Read the user's manual for Tower for a better description, but basically it checks the stiffness of the redundant by checking for a load capacity.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: Redundant member in lattice towers

(OP)
My actual version is 10.60. I don't have the option to check the redundants. I will ask to upgrade the current version. Now I have to check the redundants manually.

Have ASCE 10-97 any consideration to check the redundant who are with an angle less than 30º? Where you have to consider the aditional load of a worker with his equipment?

Thanks.

RE: Redundant member in lattice towers

Yes, if your company has paid for maintenance you should be able to upgrade to the latest version with the redundant checks. I believe the new version of ASCE 10 will have the man-load requirement in it. The theory is that redundants and main members that frame into the leg at less than 30° will be able to have a worker stand on them.

_____________________________________
I have been called "A storehouse of worthless information" many times.

RE: Redundant member in lattice towers

(OP)
Thanks!!!

RE: Redundant member in lattice towers

For heavy tower many a times redundant design is govern by % of leg load. We have to design redundant for 1.5 to 2.5 % of leg load.

Nitin

RE: Redundant member in lattice towers

The equation for redundant capacity as a percentage of main member load will be in the new edition of ASCE 10 and is already in PLS-Tower (the newer versions).

_____________________________________
I have been called "A storehouse of worthless information" many times.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources