I am in the process of looking at designing a large warehouse in accordance with IBC2009. I am currently using a R=3 and I am getting some rather large loads built up in the diaphragm (nothing that falls outside of the diaphragm values listed in your standard deck catalog). My question is in reference to the diaphragm load built up under seismic loads. Since this load is calculated at the strength level and the diaphragm tables are calculated at the allowable level, am I allowed to use 0.7E when figuring the diaphragm requirements?






RE: Seismic deck diaphragm?
ASCE 7-05 12.10.1.1 Diaphragm Design Force
Floor and roof diaphragms shal be designed to resist seismic forces from structural analysis, but shall not be less than that determined in accordance with Eq. 12.10-1.
This section further discusses limitations.
I use this value unreduced. I figure during an earthquake you do not want your deck to yield/plasticize, you want your LFRS to yield and dissapate the energy - If the deck were to plasticize and such your load transfer would change to your LFRS. So this force should be high compared to LFRS.
RE: Seismic deck diaphragm?
RE: Seismic deck diaphragm?
RE: Seismic deck diaphragm?
The code has provisions for minimum and maximum diaphragm loads so that is taken care of in the code and you don't need to further use additional loading on it.
However, you can always (and probably should be) a bit conservative with metal deck diaphragms due to large variations in fastener/weld installation quality.
RE: Seismic deck diaphragm?
RE: Seismic deck diaphragm?
RE: Seismic deck diaphragm?