Using wye PT's on 3-wire system
Using wye PT's on 3-wire system
(OP)
We have a 23kV 3-phase 3-wire system to be metered. The only available PT's are single bushing. Would it be accurate to install these in an un-grounded wye connection on the primary side and a grounded wye connection on the secondary side and use a three-phase 4-wire metering set-up? I know it is not preferred, the question is will it work?






RE: Using wye PT's on 3-wire system
Frankly, accuracy is the least of worries (not that the accuracy wouldn't be wrong too).
Single-bushing VTs, typically have the H2 (IEEE) or P2 (IEC) bonded/tied to the base plate/terminal box. That plate/terminal box is going to be grounded...either directly by the connection of a ground conductor to the VT's ground pad or indirectly by mounting the VT on a metallic structure.
I don't time/space to list all of the problems that would come from an install you describe...just don't do it.
RE: Using wye PT's on 3-wire system
RE: Using wye PT's on 3-wire system
That said, if the PT and metering voltage ratings are sufficient to withstand line to line voltages, then it is possible to use these for metering your system. The PT high side neutrals (H2) will be grounded through their mounting structure to the metering equipment grounding system. It is only necessary to measure the phase currents and phase voltages to one common point of connection of the metering voltage elements (Blondel's Theorem). That common point can be the metering system ground point as long as the metering voltage elements (PTs and metering) can withstand the possible unbalanced system voltages.
RE: Using wye PT's on 3-wire system