12. Variable speed drive application
12.1 Consideration regarding rated voltage
The stator windings of W22 motors are wound with class F insulation (class H optional) and are suitable for either DOL
starting or via a variable speed drive. They incorporate the WEG exclusive insulation system - WISE® (WEG Insulation
System Evolution) – which ensures superior electrical insulation characteristics.
The stator winding is suitable for variable speed drive application, taking into account the limits shown in table 18.
Table 18 – Limit conditions for variable frequency drive operation without application of a load reactor
Motor rated voltage | Peak voltage on motor terminals | dV/dt on motor terminals | Rise time | Time between pulses
Vn ≤ 460 V ≤ 1600 V ≤ 5200 V/μs ≥0.1 μs ≥ 6 μs
460 V < Vn ≤ 575 V ≤ 1800 V ≤ 6500 V/μs ≥ 0.1 μs ≥ 6 μs
575 V < Vn ≤ 690 V ≤ 2200 V ≤ 7800 V/μs 0.1 μs ≥ 6 μs
Notes:
1 – For the three cases above the maximum recommended
switching frequency is limited at 5 kHz. I believe that the factory default Carrier Frequency of an ACS800 drive is higher than that.
2 – If one or more of the above conditions is not followed accordingly (including the switching frequency), an output
filter (load reactor) must be installed on the output of the VSD.
3 – General purpose motors with rated voltage up to 460V may be operated by a frequency inverter respecting the
limits shown in table 18.
4 – General purpose motors which at the time of purchase did not have any indication of operation with a frequency
inverter, and with nominal voltage greater than 460 V, require special insulation to support the limits indicated in
table 18. Otherwise, the limits of the first line of the table (for nominal voltage up to 460 V) must be considered or a
load reactor at the output of the VSD must be installed.
5 – General purpose motors which at the time of purchase did not have any indication of operation with a frequency
inverter and which are the dual voltage type, for example 380/660 V and 400/690 V, may only operate driven by a
frequency inverter in the higher voltage with the installation of load reactor or otherwise respecting the
limits of the first line of the table (for nominal voltage up to 460 V).