when there's a fault and reactive current is being injected into the power system, wouldn't this reactive current contribute to the fault current?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
reactive current during a fault
|
RE: reactive current during a fault
RE: reactive current during a fault
Source impedance plays a larger role in determining power factor angle of current flowing toward the fault (when compared to a voltage phase reference upstream of that source impedance). Typically inductive (Cables, transformers).
=====================================
(2B)+(2B)' ?
RE: reactive current during a fault
RE: reactive current during a fault
The injected fault current will provide support of the voltage and of course will be only a small portion if compared to the fault current coming from the network side.
The injected fault current will increase the total fault current of course but that is one negative aspect of having a "stronger network". on the plus side this will aid in supporting the voltage!