I'm sure this is a typical detail but I haven't dealt with it and could use a point in the right direction.

I have an industrial building with an existing 6in. slab on grade. They want to put in a trench for electric, about 75 linear feet. The trench is supposed to be 6" deep x 6" wide, and have a flush removable cover. I took a look online and saw some precast systems but they seemed like overkill.

I've never done this but I was thinking of the attached sketch. Basically overcut the existing slab and provide a concrete beam, with a formed trench in the top and expansion/movement joint at each side. This will have forklifts traveling over it so it will see some decent point loads.

Is this overkill? Is there a typical detail for this that makes more sense? Do the joints at the side make sense or would it be better to provide only a normal control joint in the top 1/4 of the joint. Thanks.

RE: Trench in Existing Slab on Grade

I would want to cast the new trench with about a 2" ledge for the slab to bear on. Just requires a bit of detailed hand excavation.

RE: Trench in Existing Slab on Grade

(OP)
I like that idea. So hand excavate out a bit and cast the trench below the ex. slab on each side. What about joints between the new/old?

RE: Trench in Existing Slab on Grade

Yes, that's what I would do.

RE: Trench in Existing Slab on Grade

(OP)
What about the joint between new and old? Pour new against existing and then provide a normal control joint where the two meet?

RE: Trench in Existing Slab on Grade

Yup... but, I would slope the excavation a bit and make the trench a bit wider at the top to accommodate the sloped sides... less of a hassle of granular base sloughing in.

Dik

RE: Trench in Existing Slab on Grade

Hang on, Option 2 lost the seat for the slab. You can slope the sides a bit if necessary, but keep the seat.

I would keep the joint as you showed it before. The compressible material full depth is not really necessary, but a bond breaker is. Maybe just a sheet of plastic. Then form the recess at the top for a backer rod and sealant. High modulus polyurethane sealant to manufacturer's specification as to joint geometry and backer rod.

RE: Trench in Existing Slab on Grade

(OP)
Seat is back, with sloped sides - how about this?

RE: Trench in Existing Slab on Grade

I like it.

RE: Trench in Existing Slab on Grade

Pretty much the detail I would use, except the soil slope may be a little more towards 60 degrees for drawing just to accommodate whatever sloughing occurs.

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources