Hello all,
I am designing a natural gas pressure reducing valve system which is utilizing self-contained pressure regulators to reduce the pressure of incoming gas. The flows through the system are such that I cannot size a single regulator to control over the full range of flow (the turndown is greater than 100:1). So, I must design both a "High-flow" and "Low-flow" pressure reducing train and install them in parallel.
I believe this is commonly accomplished, however, my question is this: During cases of low flow, what will keep the larger, "High-flow" valves from chattering and trying to control pressure when the "Low-flow" valves should be operating and controlling pressure.
I believe this can be done by setting the “Low-flow” valves to a control to a higher pressure (say 130 psig) and set the “High-flow” valves to a slightly lower pressure (say 125 psig). This way, during periods of low flow, the “High-flow” valves will be closed since the “Low-flow” valves will be controlling to a higher pressure downstream. Once the system demands more flow, the pressure will drop and the “High-flow” valves will open.
Any thoughts or previous experience is always appreciated.
Regards,
GHB

RE: Natural Gas Pressure (Self-contained) Regulator Chatter

yes, your analysis/thoughts are commonly practiced.

the lower flow regulator should have the higher pressure setpoint than the high-flow regulator as you so describe. the difference in setpoints may need be verified/tested, but 5-7-psi is adequate for similar systems i'm aware of.

good luck!
-pmover

RE: Natural Gas Pressure (Self-contained) Regulator Chatter

Include the "droop" in your analysis of the regulators if it's significant. Droop isn't significant for all regulators but if it is, you can get a surprisingly wide range between what the regulator will 'control' the pressure at between min flow and max flow compared to set point.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources