with a 1 1/2" dia pipe for the railing, the H/R post is the weak link....the post spacing is governed by the uniform load of 50 lbs/ft on top rail.....for indusrtial bldgs(non-public access) the 50 #/ft seems excessive to me....I would appreciate some feedback on how other engineers are addressing this, especially for non-public access buildings...thanks for your help..

RE: Handrail Loading

That limit (actually 200 lbs force minimum on one vertical support, 50 lbs/ft average works only if you have one support per four feet. Otherwise, you may have even more force on the support.) is in the rules.

Live with it.

For outside forces loaded from wind under unusual circumstances - a balcony with "solid" faces like a glass panel under hurricane loads - the "handrail force" from people abusing the handrail may be less than the wind load. Then again, you would not expect people to be crowding a outside handrail under hurricane-force winds, so the two should not be additive. ......

RE: Handrail Loading

In NYS building code, if occupancy is a certain category, handrail load can be reduced to 20 PLF or 200#.

RE: Handrail Loading

(OP)
does anyone know the rationale behind this 50#/ft?...I can see it maybe occuring on a crowded balconcony or panic situation in a public place...but, just leaning with one's elbows on the railing, shoulder to shoulder, can't see it generating this kind of load...understandably,the codes try to cover the most extreme load case that may occur less than 1% of the time and only in certain bldgs....I guess where I am going with this is that the engineer should be able use use his engineering judgement and not use the codes as a cookbook...

RE: Handrail Loading

Check IBC 2009 - 1607.7.1 - Exception 2. It allows only 20 plf. Not sure what your governing building code is. I have seen PIP standard details (SF05520)...I haven't checked, but I have doubts about their ability to meet the criteria you are trying to design for. These standard details are routinely used in industrial settings.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources