Have a competing bid to put cpvc in a restaurant. We bid black steel pipe. Have never seen cpvc in a restaurant before. Can it be done?

RE: CPVC

It can be done in the light hazard area. If the kitchen is under 800 sq ft, you can use CPVC above that. If it is wood construction, you will need specially listed sprinklers to allow the use of CPVC.

You just need to review the datasheet for Blazemaster pipe to get all of the listings that are appropriate.

Travis Mack
MFP Design, LLC
www.mfpdesign.com