Trench Rescue Shoring
I am assisting some local fire department personnel trying to wade through what is needed for trench rescue shoring. This would be shoring that the firefighters/rescue personnel assemble to go into a trench that most likely collapsed to try to rescue a victim. This would be short term shoring meant for a matter of hours to maybe a day (after more than a few hours, things will shift to recovery and change the urgency and the willingness to take risks). There isn't really much of a standard for this stuff and some of what is taught to rescuers in classes seems questionable at best.
My background is structural, so I am ok for half of the system. Most of the departments use 3/4" finform panels with a 10' long, 2x12 strongback installed down the center of the panel - this seems to be an offshoot from text in OSHA. They then place some struts, commonly pneumatic, between the trench walls. Paratech and Prospan seem to be pretty common. They are placed with 100 psi to 250 psi air pressure on a 2" or 3" diameter strut (say 1,000 to 2,000 pounds of force maximum pushing into the walls).
A statement that I keep running into is: "Shoring is designed to prevent soil from moving. No shoring can hold back the weight of collapsing earth." This is usually followed by the "soil arching effect" further into the piece I am reading. One manufacturer suggests that the pressure that the pneumatic strut places on the soil creates the arching effect and stabilizes the trench walls so that they don't begin to move. They further go on to say that in good and decent soils, the struts can be placed in the trench without any panels of any type, just a 8"x12" foot on the strut ends and the rest of the earth is completely unsupported. In poor soils they suggest panels with 100% contact with the trench wall which would seem impossible in a rescue situation. I also read commonly that the panels cannot be considered a structural member, although I don't understand why.
To me, shoring a trench for rescue seems somewhat similar to soldier pile with lagging in theory (i know there isn't embedment and it will behave differently), however, most guides say that even though there is soil arching between the soldier piles, there is still force (a reduced force) on the lagging between the piles. Caltrans Trenching and Shoring Manual says that this force is about 60% of the active earth and seems to max out at about 400psf. With this case, it would seem that any unsupported soil between the struts could still be at risk of collapse even if an "Arching Effect" was present.
What I am wondering, is there any sound information that would indicate what magnitude of force would be necessary to create soil arching in the walls of an excavated trench?
If so, how would you calculate how much force a strut would have to place on a trench wall in order to create the arch effect?
Even if the soil arches, is the soil between the struts adequately supported as to not have to protect it?
And lastly - even if the arching effect is reasonable, would you consider it safe to use struts without panels to enter the trench?
Thanks for any help!!
RE: Trench Rescue Shoring
You can find the background notes in nearly all Foundation Engineering Books. Look for "Barced Cuts" or "Braced Excavations" under chapter titles. I would insist on timber or steel plate lagging and no exposed side soils. The best coverage of this topic is in "Foundation Design" Teng, 1962, Chapter 13. Here both the geotechnical analysis and the structural design is covered. Look at the attached loading diagram as an example of the imposed earth pressure.
In situations where time is essential, you don't have time to play with timber lagging and so on. Have a look at this website : www.krings.com. I believe you rescue team should be equipped with a truck with its own crane and some of this krings equipment and a trailor with a small tracked excavator.
YOu may want to look into 'pre-fabbed' excavation cages to be lowered in place. These can be loaded on a trailer, ready for use at a moment's notice.
Dik
I think I rambled on too much in my initial post.
My question wasn't about how to accomplish the task, but more about how to analyze the specialized systems that are currently available, specifically as it relates to soil arching. How much force would have to be placed on the trench walls at strut locations to create a soil arching effect between the struts? Does anyone have any ideas on how this necessary force could be calculated for clay soils?
The soil will arch between vertical beams and the lagging pressure is only a function of Ka, soil unit weight and the horizontal span between the vertical beams. The struct force is only due to soil & water pressure and surcharges. That is why you need a steel plate or timber lagging, concrete lagging, etc to transfer the lagging pressure due to arching to the soldier beam or sheetpile. I have attached a document that shows you one method of calculating lagging soil pressure.
To get your strut force, let us say, you have 3 struts in a 20 ft excavation. Let us say that the struts are at -3 ft, -9 ft and -15 ft. For simplicity, let us say the earth pressure is trapezoidal and the vertical supports are at 6 ft horizontal spacing. You load the beam with the combined earth and surcharge pressure and make your struts the support reactions. Then just solve for the 3 reactions. Many publications, however, mention that real life measured strut forces reveal that the upper strut will see higher force than we can calculate it with a continuous beam method.
You will not have time to assess which method to use for each event, so the answer should be for the generally applicable case. Loose or saturated soils (the conditions frequently leading to trench collapse) will likely be present.
I would be inclined to use the same methods as the US&R FOG/SOG use for shoring. Although it is not specifically shown for trench shoring, it is the method that should be known by the responders.
If you don't know the disasterengineer.org website, go here and get the FOG and/or SOG:
http://www.disasterengineer.org/Library/tabid/57/D...
Solid walls would be mandatory since you cannot expect compacted soils and arch action, and treatment of the soil as a fluid may be excessive, but might be necessary following a collapse. Consider this as a basement wall with cohesionless fill, in our normal engineering vernacular.
You mention a plywood panel (or similar) with a 2x12 strongback. I'm not sure a 2x12 flat on the plywood does more than provide a bearing surface for the struts and maybe distribute the pressure across a wider area, and a 2x12 on edge would be a disaster if it rolled. I'm just not clear about your description.
If you are not familiar with the US&R shoring methods (as I wasn't until recently), look around the Disaster Engineer website.