Two-way or one-way concrete slab system?
Two-way or one-way concrete slab system?
(OP)
Dear all,
I have a concrete floor system with 8m x 7m bays with a 2.5m slab cantilever at the perimeter. I can only run beams parallel to the 8m span.
I am wondering if by simply adding a 'stiff' beam parallel to the 8m span, I can design the slabs as a one-way system perpendicular to the beam.
What would constitute a 'stiff' beam and wouldn't that mean I can expect significant cracking before the two-way distribution would turn into a one-way distribution?
I would prefer to have slab-bands instead of a deeper beam (headroom restriction), but surely I can not design for a one-way slab condition with a shallow slab-band albeit wider than the concrete beam, can I?
Also, any special considerations when having a 2.5m long cantilever at the perimeter of the floor system?
Would really appreciate some guidance on this topic.
Thanks!
I have a concrete floor system with 8m x 7m bays with a 2.5m slab cantilever at the perimeter. I can only run beams parallel to the 8m span.
I am wondering if by simply adding a 'stiff' beam parallel to the 8m span, I can design the slabs as a one-way system perpendicular to the beam.
What would constitute a 'stiff' beam and wouldn't that mean I can expect significant cracking before the two-way distribution would turn into a one-way distribution?
I would prefer to have slab-bands instead of a deeper beam (headroom restriction), but surely I can not design for a one-way slab condition with a shallow slab-band albeit wider than the concrete beam, can I?
Also, any special considerations when having a 2.5m long cantilever at the perimeter of the floor system?
Would really appreciate some guidance on this topic.
Thanks!






RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
Thanks for the advice.
slickdeals,
I absolutely agree. I've done a FEA analysis of this and can confirm that even with a reasonably sized slab band, two-way distribution is still very dominant. Can someone elaborate how we can justify a one-way slab design?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
You see this in your beam-slab system designs where engineers will include:
1. Traditional transverse temp/shrinkage reinforcement
2. Heavier T/S reinforcement near ends of beams where 2-way cross stresses occur
3. Diagonal bars extending from the outer beam faces at corners towards the center of the slab to control diagonal cracking at the corners.
RE: Two-way or one-way concrete slab system?
The band beam and slab system is used here either conventionally reinforced or post-tensioned (generally with partial prestressing). It also lends itself to the use of steel form deck for both the bands and slabs. Another version uses precast form panels (one proprietary system is called Humeslab), which have bottom reinforcement cast in.
RE: Two-way or one-way concrete slab system?
The reason that Finite element doesn't catch the one-way slab behavior correctly without manipulation can be due to a number of items. The most common is the stiffness of the beam compared to the slab. If the beam and slab are not modeled with the correct stiffness due to reo than the results will be skewed. Generally the beams should be stiffer by a factor of 4ish. This stiffness should also include the stiffness due to T and L beam framing. This is often ignored if plate elements are used with centroids matching and should be adjusted by experience.
I could also go into the other assumptions into the creep and shrinkage differential ect but I am sure that will bore most people.
in other words I agree with Hokie66.
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: Two-way or one-way concrete slab system?
hokie66, I'm a bit hesitant to take the slab span as the clear distance between the bands as opposed to the center to center distance of the bands. Am I out to lunch on this?
RE: Two-way or one-way concrete slab system?
RE: Two-way or one-way concrete slab system?
So please find attached screen shots from three different model types.
from the pdf you can see with the 1'st model that the My moments are very small in the model compared to the beam moments, this is to be expected and shows that the finite model can be corrected to show the one way action. The second model dose not capture the reduction in the my moment as well, this is due to the beams being modeled as beam elements, beam elements are really only good is you include offsets to the edge of the beam or the beam is narrow. The 3'rd model is a straight flat slab.
For the 1'st model which is the model I would recommend is modelling in Finite elements package.
I have not looked at any of my assumptions in this modelling for example the column moments are assumed fully fixed. I have only shown the My because that is what we are interested mostly.