Instantaneous Override Current (ABB Tmax)

Instantaneous Override Current (ABB Tmax)

Instantaneous Override Current (ABB Tmax)

(OP)
Hi, does anyone know what the instantaneous override current of an ABB Tmax T4S circuit breaker with PR222 trip unit is? I cannot seem to find an ABB document which has this.

RE: Instantaneous Override Current (ABB Tmax)

override current??

RE: Instantaneous Override Current (ABB Tmax)

The trip unit may not be equipped with instantaneous override. You should contact your ABB representative for confirmation.

RE: Instantaneous Override Current (ABB Tmax)

I checked my EasyPower breaker library data. It does not show an instantaneous override being available for this breaker + trip unit. The maximum instantaneous setting is 12X.

RE: Instantaneous Override Current (ABB Tmax)

(OP)
The reason I though it might have one is that in the ABB white paper "Working with the Trip Characteristic Curves of ABB SACE Low Voltage Circuit-Breakers" Figure 13 shows a TCC of the PR222DS/P-LSIG (with Tmax T4H250 CB) with I protection not activated. In the figure, the Instantaneous Override appears to cut into the short time curve at 3kA.

RE: Instantaneous Override Current (ABB Tmax)

In the IEC world, it may well be different. The "identical" trip unit in the US can be configured differently from the equivalent IEC version due to differing codes and standards.

In my previous message I was referring to US equipment - I should have been more specific.

RE: Instantaneous Override Current (ABB Tmax)

The ABB trip unit PR222DS Instantaneous (I3) setting range is from 1.5 to 12 x In.
There is no OFF setting on the PR222DS Instantaneous element.
Some ACBs have an OFF setting on the Instantaneous element, however if the current approaches the breaker interrupt rating Icu or Ics, the Instantaneous element will automatically operate.

RE: Instantaneous Override Current (ABB Tmax)

Is this a UL or an IEC application? It can make a difference. Also, some new circuit breakers can be purchased as molded case circuit breakers or as low voltage power circuit breakers just by changing a part number. This will also impact the available options on the instantaneous settings.

If this is built to UL molded case circuit breaker standards, it will have an instantaneous trip (either by setting or override)

RE: Instantaneous Override Current (ABB Tmax)

(OP)
It is an IEC Application.

RE: Instantaneous Override Current (ABB Tmax)

Then you can probably ignore anything that those of us in the US have been telling you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources