Code Requirements for Air Handling Units

Code Requirements for Air Handling Units

Code Requirements for Air Handling Units

(OP)
We have an Air Handling unit which we have recently converted from steam to Natural Gas by replacing the steam coils with the Indirect Fired heat exchanger. The unit is 60,000 cfm. We want to install smoke detectors in it, 2 before the heat exchanger and 1 before the fan. I just wanted to know that installing these smoke detectors falls under which code? If somebody could tell me exactly that would be really appreciated.

P.S I am looking for Canadian Codes. Thanks

RE: Code Requirements for Air Handling Units

Smoke detectors are required in the return side by the IMC 606.2.1. I'm not sure, but I think NFPA 90 has some requirements for detectors as well.

RE: Code Requirements for Air Handling Units

(OP)
You are right. Smoke detectors are required in Air Conditioning and Ventilation systems having a capacity greater than 2000 cfm.
Thanks a lot.

RE: Code Requirements for Air Handling Units

So, you picked up the code and answered your own question..........?????
Start with the code next time.........

RE: Code Requirements for Air Handling Units

The Florida Building Code requires the smoke detector in the supply, to protect against fires in the HVAC system and outside air. Area detectors protect inside. NFPA gives additional guidance on placement in supply or return.

RE: Code Requirements for Air Handling Units

You should also read the section of NFPA 90 about units above 15,000 CFM.

Justin K, P.E.
http://www.engproguides.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources