13r and taking the increases per ibc
13r and taking the increases per ibc
(OP)
I have a project that consists of one three story apartment building. On the building code sheet it looks as though they took some increases for a sprinklered building. My question is if they took the allowences can you still do a 13R system or does it have to be a full 13?





RE: 13r and taking the increases per ibc
http://www.eng-tips.com/viewthread.cfm?qid=331744
RE: 13r and taking the increases per ibc
In order for the architect to take an area increase by use of the fire sprinkler system, you get sent to 903.3.1.1. Therefore, you go full 13.
Travis Mack
MFP Design, LLC
www.mfpdesign.com