Rupture Disk Reliability
I am looking for reliability # for RDs. The one i am interested has a size of 10", and set pressure of 11 psig installed on a pipe that is filled w water. Furthermore I appreciate if you can provide a reference that lists the such reliability #s for different sizes/set pressures. For my application i need a reliable pressure device that would not fail below its set pressure.
RE: Rupture Disk Reliability
What you need to look at is set pressure of the rupture disk and Maximum Operating pressure of the Rupture Disk. That is where you are going to have problem.
Differnt RD styles have different tollerances between the Set, or Burst pressure and the Maximum operating pressure. Some require the MOP to be less than 70% of Burst others you can go as high as 90%. But such a large disk and a low pressure I think you are going to be in trouble.
Stonecold
There are publications available which identify Probability of Failure on Demand (PFD) for safety devices such as relief valves. Based on the simplicity of rupture discs compared to the rather complex construction of safety relief valves where often up to several dozens of individual parts need to flawlessly interact to assure operation then rupture discs are often considered to have higher reliability then safety valve. This is often expressed in SIL (safety Integrity Level) with safety valves classified at SIL 1 and rupture discs at SIL 2.
Hope this helps
Roger B
Pick up that 2,000 lb phone and CALL a mfg. They will be VERY happy to help!!