Wiel McLean Model 88 series 2 installation

Wiel McLean Model 88 series 2 installation

Wiel McLean Model 88 series 2 installation

(OP)
I have two new low pressure steam (steam pressure set to 8 psig) boilers operating in parallel. These boiler have independent piping leading to separate pressure reducing valves. The valves are set to system pressure of 5 psig. Downstream of the PRV's is a steam header and off the header the steam travels to various zones.

Intermittently, after a burner shuts down, we have noticed that the steam pressure continues to build in boiler #2. It has opened the high pressure safety limit (set to 13 psig) several times. This results in a nuisance trip and alarms our local idiot light.
Boiler #1 does not exhibit this problem.

We have investigated the burner control and it is shutting off the gas valve when it should. Both burners have independent control systems. Where do we get the extra prssure from??

Any ideas,
Thank you,
Tom

RE: Wiel McLean Model 88 series 2 installation

how old are the boilers? how is the water quality? are the safety devices inspected yearly (i.e. removed, inspected, cleaned, etc.)?

as strange as it may seem, but if the water quality is poor, the solids can/may collect and adhere to the cast iron section walls. thus, the solid matter is still hot enough to generate steam once the fuel is shutoff. eventually, the cast iron sections will crack due to excessive heat (poor heat transfer). then again, i've seen cracked cast iron sections filled with scale and not leak. if the boiler is cleaned regularly &/or has excellent water quality, then this is likely not the problem.

are you sure the PRV (pressure reducing valve?) is working properly?

is the pressure relief valve (safety) connection clean and free of solid matter?

hope this helps.
-pmover

RE: Wiel McLean Model 88 series 2 installation

(OP)
thanks, pmover

the boilers are new 2.5 MBTU replacing older boilers
and the issue has been happening since start-up last spring..
all other accessories are new,
water quality is within specs,
thx,

RE: Wiel McLean Model 88 series 2 installation

Is the boiler shutting down because of reduced demand?
I suspect that the tuning constants for the two boiler controllers are different.
Leading boiler #2 to shut off too late and resulting in the overshoot condition.
Look at the controls.

= = = = = = = = = = = = = = = = = = = =
Plymouth Tube

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources