I am doing an analysis on a building from the mid 1960's. I have a floor framing plan that references Ceco "14W4" or "14H4" bar joists. Span is 20ft. Can anybody tell me what the allowable uniform load might be or point me to a site that has a catalog for these joists?
KrisL
I am doing an analysis on a building from the mid 1960's. I have a floor framing plan that references Ceco "14W4" or "14H4" bar joists. Span is 20ft. Can anybody tell me what the allowable uniform load might be or point me to a site that has a catalog for these joists?
KrisL






RE: Ceco Joists
a maximum resisting moment of 212,000 in.#,
a maximum end reaction of 3500#,
a total load of 350 plf,
and an L/360 live load of 245 plf.
Hope this helps.
Mike McCann
MMC Engineering