(OP)
We currently have CDEGS Multiground with MALT program, is MALZ program required for Substation Grounding Analysis?

RE: CDEGs MALT and MALZ program

It's been a long time but I remember using RESAP and MALZ when performing ground grid analyses.

RE: CDEGs MALT and MALZ program

MALT assumes that the potential at all points of the ground grid is the same. MALZ provides for voltage drops in the grid conductors. There can be a difference in large grids if the soil resistivity is low, but normally MALT is adequate for normal step- and toudh-voltage calculations. If there is a difference in grid potential, then the location of the fault is important, so it complicates the analysis.

MALZ also is needed to analyze high frequencies such as lightning.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources