Weld Flange To Dish Head Directly
Dear All,
I have 1 question which cannot be solve and would like to ask for dear forum members's opinions:
Design condition:
Internal pressure : 10 bar
Torispherical Dish Head: OD1300mm ( around 51")
SORF 20" Flange Ansi 150 -->OD about 700mm (27.5")
I would like to open an opening in center of the dish head and weld this flange directly on it using welding method just like Fig UW-16.1(c) without any nozzle.
How do i calculate to know if the opening is properly reinforced?
I checked UG-36 (b) (2) but i see none of the figure in Fig UG-36 similar to my case.
I checked Appendix 1-7 (LARGE OPENING IN CYLINDRICAL AND CONICAL SHELL) but it was for opening in shell not head.
I checked Appendix 1-10 (ALTERNATIVE METHOD FOR DESIGN OF REINFORCEMENT FOR OPENING S IN CYLINDRICAL AND CONICAL SHELLS UNDER INTERNAL PRESSURE) still was for shell not head.
I really hope for a reply that could help me. Thanks in advance.
The flange will be closed with blind flange in the end of the fabrication.
Design condition:
RE: Weld Flange To Dish Head Directly
It would be better if you provide a sketch of your setup just to make sure it is understood correctly.
prex
http://www.xcalcs.com : Online engineering calculations
http://www.megamag.it : Magnetic brakes and launchers for fun rides
http://www.levitans.com : Air bearing pads
Mike
Why I am asking to neglect the area contributed by the nozzle neck (that is hub of SORF is your case), because I am sure limit of reinforcement normal to the vessel wall falls beyond the hub length, so I am neglecting area A2.
Since your opening and its limit of reinforcement as set by UG-40 falls withing the spherical portion of the head tr (when used in reinforcement calculations) shall be the thickness of the sphere not that of tori-spherical head, this will help you in increasing area A1.
Please run the calculations and then share the results. It is better to perform manual calculations in this case.
Nasir
Welding Engineer
DESCON ENGINEERING LIMITED
PAKISTAN
Do = 1300mm (vessel/Torihead OD)
Minimum thk of vessel tr= 11.5184mm (As per UG-27)
Head wall thk t = 15mm (I use 15mm plate)
Nozzle wall thk tn = 93.45mm ((OD of flange - ID of Flange)/2)
Required nozzle wall thk trn = 4.548mm (Calculated as per UG-27) Corrosion Allowance = 1mm
F = 1
fr1,fr2,fr3,fr4 = 1
E1 = 1
Sn,Sv,Sp = 108000 kpa
A= 5910.7
A1= 1786.43
A2=6667.65
A3=Not Applicable (I does not thrust the flange beyond the ID of the flange)
A41=225 (leg^2)
A42= Not Applicable (since i assume no reinforcement pad)
A43= Not Applicable since no inward nozzle weld
As per Figure UG-37.1
A1+A2+A3+A41+A43 >= A
8679.07 > 5910 (Opening is adequately reinforced).
The reason i use A2 because currently i assume the flange as nozzle. My logical thinking tell me to include the A2. Feel free to comment on the calculation.
How are you going to seal the pressure at the bolt holes?
I suggest you use a studding outlet.
http://www.texasflange.com/Studding%20Outlets/Stud...
Am I missing something? All you need in fact is a forged studded connection UG-43(d) and as per Fig UG-40, item a-2. Do you HAVE to use a SO flange? If so, hpw do you intend to bolt the cover and seal the bolt holes, from inside?
gr2vessels
I got 2 ways to solve this:
1) Cut small Round plate around 6mmt~10mmt(for me i will see the what scrap metal i had) plate: fill the hole with the plate then GTAW the plate from outside.
2) Cut a plate that OD same as the flange OD and in the center, cut open an ID hole (probably a little bigger than the ID of the Flange) and weld from the bottom of the flange to seal off all the bolt hole.
I will do Dye Penetrant test afterwards to check for any visual defect.
doct9960 beat me on the stroke of keyboard, but the question is not only how you make it, it is how (and why) would you design a such a complicated and questionable flanging method, when you have the code recommendation and standard studded flanges designed and made for your particular application.
By the way, you still have to design a revolutionary new bolting method and explain your AI why did you used that. I bet you also thought of welding some studs in the existing holes, then do the calcs for that arrangement, right? How you going to do the calculations for this flange, which does not comply any longer with any standard flange??
Cheers,
gr2vessels
My area does not sell any "standard studded flanges", thats why i choose to use a more common sorf flanges. Yes, you are right, i will weld the stud in the existing hole. In my opinion, i will do some calculation for the opening reinforcement requirement as per what i do above. As for the blind flanges thickness, i will reconfirmed the thickness of the blind using UG-34(c)(2) and C equal to the value of Figure UG-34(p) which i found nearest to my design. For the thickness required for the flanges to be used, i am still scratching my head to work it out(still flipping the code book now :P), in the same time hope fellow forum member to throw in some idea which we can discuss.
I start to think to use a plate which i cut it round shape same as flange OD, drill some bolt hole (not through hole), tapping it. For the thickness calculation i think i can use UG-27.
The thickness of your insert flange should be dictated by the depth of the bolt holes, just make sure that the flange encompasses the head wall as extended to the flange ID.
Your calculation seems correct in the principle, but I didn't check the figures. As a minor correction, you should take out the corrosion allowance on the inside diameter. Also tr, as pointed out by Fizza453, can be calculated as the thickness of a sphere per 1-4(d) with M=1.
prex
There is 1 question about the tr, shouldn't i use UG-32(e) for the thickness calculation? When shall i use 1-4(d) method? Is there any specific condition i missed out or is it 1-4(d)?
tr using UG-32 is 11.518mm
tr using 1-4(d) is 8.02mm
Oh ya, for the welding stud to flange issue, is it possible we use stud as the filling material to fill the bolt hole of the flanges for my case? After inserting the stud where the surface of the stud is same level as the bottom face of the bolt hole, and then we weld it(both top(fillet weld) and bottom (GTAW)of the flange. If that is possiblt, i may dictate the thickness of the flange by its thickness rather than the depth of the bolt holes.
My vessel is subjected to internal pressure only: Design pressure is 10 bar.
With Joint Efficiency = 0.85
Please do not refer any more to the studs welded into the holes, it is certainly not acceptable to code, and for more than one reason. If you want to do that, please don't tell us, we like to have relationships here with real and experienced engineers. If you insist I'll have to ask the maintainers of this site to delete this thread.
prex
Thanks for the clarification. There is a lot of thing i am still learning, therefore i am keep asking for opinion and from more experience engineer in this forum. For my cases, i try to ask every possibilities i can think of with the hope that more experience engineer can provide a good guideline so that we all can learn from it. it is not that i want to influence other people to accept my method. From my reply you can read that i keep asking and giving out my idea with code to back me up. For the stud issue , i am asking for the opinion of the forum members to to see if any other member had been try the method or maybe some case study which we nvr encounter in our engineering life. You never know if you never ask. Please don't be too aggresive when you think other people is trying some new idea or asking for help.
Third, don't.
Mike
prex
I found that UW-16(3) quite near to addressing to my cases, "the opening shall be reinfoced in accordance to UG-37 and the nozzle or other connection attached using a suitable detail in Fig-16.1,if welded." However, no matter how i find, none of the figure look as similar as Fig 40(a-2) just like gr2vessels told me. But from the UW-16(3) statement, i believe calculating the reinforcement required for my case using UG-37 should be correct.Just a matter of time before i can work out the correct way to find the real answer.
Mike
Out of curiosity...
Why can't you place a 20" pipe/plate neck on your 20" SORF flange?
Why do you need a manway at the bottom head? Why not on the cylindrical shell?
Is your vessel going to be U-stamped? In what part of the world will this vessel be installed?
1st: To cut cost. I may be suffer from engineering calculation initially but if i can cut cost by saving the cost of the project, i will try my best to do it.
2nd: The bottom of the tank required a manway because there is a baffle plate near the bottom of the tank which to be bolted with some bolting equipment require human to do servicing ( unbolting the nut from the bottom of the tank) in the future.
3rd: It does not require U-stamp by the client but the local government require us to submit a valid calculation based on ASME code in the fabrication of this vessel.
4th: This vessel will go many places (a lot of units in the future) but particularly in the asia like singapore,indonesia,malaysia, and thailand.
Mike
The way to seal the bolt hole is an idea only,after long discussion in this forum ultimately i think cutting a plate, drill and tap hole would be more practical and faster than sealing a bolt hole and using flange. I would like to thanks gr2vessels for his idea.
The following are pressure vessel regulations stipulated in current codes:
Plate cannot be used for the size of your flange, it has to be a forging, fully tested in fabrication. You have to design the flange as per ASME VIII-1 Appx. 2 or similar code. You cannot drill through the flange and tap the hole, exposing the thread to the internal pressure. You must design it with a minimum thickness under the bolt hole to withstand the design conditions. In other words, you have to reinvent a standard flange, called studding outlet. You might make it a bit thinner and lighter, based on your particular design conditions, but the cost of fabrication will make it impractical.
Cheers,
gr2vessels
It concerns me that you are in a jurisdiction that allows pressure vessels to be manufactured without U stamp certification. There is a reason for U-Stamps and there is a reason for codes and recommended practices: They save lives. Why try to change or go around years and years of knowledge/experience.? Cost saving..?? Cheap products are just that, CHEAP and 99% of the time not worth the money spent. In this case potentially deadly.
You came here for opinion, this is mine.
Build it right and promote that fact.
stk