Question: Installing power line monitoring equipment

Question: Installing power line monitoring equipment

Question: Installing power line monitoring equipment

(OP)
I've read the followiong caution on a few commercial power line monitors.

"Caution: Do not install this ddvice on any outlet that does NOT have at least 10 meters of wire between the electrical outlet and the electrical service panel"

Can someone explain the reasoning behind this caution?

RE: Question: Installing power line monitoring equipment

Probably about prospective short circuit current. Rather unusual, I think. What device is it?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Question: Installing power line monitoring equipment

Often a requirement when MOVs are present in the device. MOVs require impedance in the supply to prevent their destruction during over-voltage transients.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Question: Installing power line monitoring equipment

The device is likely CAT II rated. CAT III would be needed on for measurements on the service panel. See the power point for a good explanation of the transient voltage withstand ratings for meters.

www.lanl.gov/safety/electrical/docs/electrical_mea...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources