Number of sprinklers on a branch line?

Number of sprinklers on a branch line?

Number of sprinklers on a branch line?

(OP)
I think there used to be a limit of the number of sprinklers on a branch line (say 8).
It may have been only for schedule pipe sizing.
I can't find the requirment in the current standards (NFPA 13 i.e. 2007).
Is it still there?

RE: Number of sprinklers on a branch line?

No. You can have as many heads on a line as can be proven with hydraulic calculations.

RE: Number of sprinklers on a branch line?

I am not a sprinkler designer, and only periodically fire up my hydraulic software, but yes, there is definitely a limit to the number of heads allowed on a branchline.

Use the skew formula to determine this. I have not checked for many years, but it should be in NFPA 13. Its 1.4 x square root of the remote area. Note: I believe NFPA is 1.4, and FM notes 1.2, but i will let you confirm that. For example if you have a 2,000 sq ft remote area, using this formula gives you 54 ft. If you are using 10 ft line spacing, you therefore can have a max of 5 heads per line.

For ESFR, you are limited to 4 heads per line. For the typical 12 head ESFR design area, it is therefore 4 heads on 3 lines.

This is important. Fires dont grow in one dimension. These rules make sure designers are applying remote areas that most closely resemble a someshat cirucular fire growth pattern.

RE: Number of sprinklers on a branch line?

Sorry, but the above statement by Sdpaddler50 is incorrect. NFPA 13 does not put a limit on the number of sprinklers on a branch line. You can have as many as you can calculate. If I have a gridded system with branch lines 200' long between mains and 10' on center, I am going to have 20 heads on that line. That is not a problem. I can have a tree system as well with any number of heads on the branch line.

There is a practical limit just due to the size of pipe that may be involved. But, NFPA 13 does not have a limit anywhere in the standard on the number of sprinklers per line.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

RE: Number of sprinklers on a branch line?

Yes, my bad. I was referring to the number of heads than can be calculated per branchline. When the OP said 8 heads, i thought he was referring to remote areas for hydraulic calculations. My mistake.

RE: Number of sprinklers on a branch line?

No problem. I just wanted to make sure that no one was confused.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources