is it possible that there is no pressure drop(no leakage) in a piping system(regardless of its size) after being pressurised for 24hrs?

RE: Is it possible?

If you did your job right, it should be the expected result.
Finally got it right?

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek

RE: Is it possible?

No pressure change at all in 24 hours? Zero leakage is certainly possible and fairly normal (most piping systems do not leak). For the pressure to not change with temperature variations id in my experience highly unlikely.

David Simpson, PE
MuleShoe Engineering

"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.

RE: Is it possible?

So, it's one of those fake leaks then, or it leaked just enough to compensate for the temperature rise?

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek

RE: Is it possible?

Would make sense if the pressure drop/rise was porportional to the temperature drop/rise.

RE: Is it possible?

It would make sense, if it wasn't so highly unlikely, and he might have even found the leak, if that happened.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek

RE: Is it possible?

I had a guy once that reported EXACTLY the same separator pressure month after month after month. I met him on location and opened the needle valve on the gauge and the trapped pressure was replaced by process pressure. When I see unchanging pressure I assume instrument error, not major coincidence.

David Simpson, PE
MuleShoe Engineering

"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.

RE: Is it possible?

Or closed instrument isolation valve.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek

RE: Is it possible?

(OP)
The pressure did drop I'm just asking because theoretically it is a closed system loop and no drop should occur but I know that theory and application are two different things so I had to ask. Besides the leakage(pressure drop) was within limits approved by ASPE.

RE: Is it possible?

I'm not at all sure what "theory" you are referencing, but it isn't valid. "Pressure" is measure of one facet of total energy of a mass of fluid. The other facets are temperature, fluid composition, and volume. In your closed system, the only one of these parameters that is constant is volume. If mass leaks out then you are going to change pressure, temperature, and possibly fluid composition. On the other hand if temperature changes, then with constant fluid composition and constant volume, pressure is the only thing left to change and it does. For a system that is pure-water full (no air pockets), a change in pressure of 1°F corresponds to a pressure change of about 100 psi. Consequently, minuscule temperature changes (day to night in a 24 hour test) can make a pressure chart look like silhouette of the Rocky Mountains.

Temperature stratification further complicates this interaction. For example if you have a large fabrication that is partly in the sun and partly in the shade (or buried) then the part in the sun will heat rapidly and natural convection will bring cooler water into the sun and push the hot water into the shade. The local pressure change will be very high, but it is not supported by the bulk of the fluid and much of the pressure change is masked in the bulk modulus of the unaffected water.

This is one of the main reasons that 24 hour tests have fallen out of favor.

David Simpson, PE
MuleShoe Engineering

"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.

RE: Is it possible?

No worries.

"People will work for you with blood and sweat and tears if they work for what they believe in......" - Simon Sinek

RE: Is it possible?

Was it a buried piping system? That is about the only way you could ever approach constant pressure over a long time span - no sun, no ambient.

rmw

RE: Is it possible?

yes , that right there mustn't be anypresure loss

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources