Sagging floor trusses in condo
I live in a condo in which the floor trusses deflect by as much as 1.5" over 6'. The two worst areas are at the ends of an interior, weight-bearing wall that runs lengthwise in the middle of the condo across the first floor. Last year after complaining to my HOA, their SE designed a fix that included jacking up the floor and then installing plywood gussets to the floor trusses. Unfortunately, the HOA was unwilling to jack up the floor for fear of collateral damage, but they did go ahead with the plywood gussets, which are now glued and nailed to the trusses.
Now I am still stuck with an unlevel floor and would like to find a fix. One contractor suggested removing the gussets, jacking-up the floor and then re-installing the gussets. I wonder how much damage this would do to the trusses. Another contractor suggested removing the plywood subfloor, shimming the top of the trusses and replacing the plywood. A third contractor suggested installing shimmed sleepers on top of the plywood and then adding another layer of plywood on top. Yet another contractor suggested first installing a wall in the finished basement and then fixing the floor from the top.
The HOA has washed their hands of the problem. I would have to sue them to get any further help from them. Since this is a condo, I am reluctant to invest large amounts in a fix, but on the other hand, think I need a level floor to sell the place. Any suggestions?
Dave
P.S. The trusses are 12" high and the longest spans are 20'. The condo is 25 years old and there is no evidence that the floor has been sinking further over at least the last 10 years - no cracks in tile or walls.
Dave
RE: Sagging floor trusses in condo
1. I feel your pain dealing with HOAs, good luck on that front.
2. I don't like the idea of installing a load bearing wall below, this has the nasty tendency that in the future some other poor bloke will decide to "open up" the space below by removing the wall, and suddenly they have the problem all over again.
3. With the trusses already reinforced so that they can handle the new floor loading without further sagging, then building up and leveling from above is not the worst solution. it should be the least costly option.
4. If the joists are going to sag under the new loading, then I'd look to remove the gussets, jack up the trusses, and reinforce, sister, etc. as needed to get the floor system strong and stiff enough to not sag any more. Find a contractor and engineer experienced in this work, typically they will jack the floor slightly over level, then reinforce the trusses, and then finally remove the jacks, at which point the floor should relax down slightly and draw the load into the newly reinforced trusses.
5. I'd get a Structural Engineer out to determine which of the above is the best option. It seems like the association's Engineer might not be the worst option, only now you'll be footing the bill.
M.S. Structural Engineering
Licensed Structural Engineer and Licensed Professional Engineer (Illinois)
The simplest is leveling compound not sure what kind of floor finish you are looking for. It's like a rather thick cement type mix that you just pour and level. Takes a bit of a good eye and techniques but works well.
That said - you will need an engineer to see if the floor can accept the extra weigth. But the other solutions while quite good and commonly done also add weigtht.
The interior bearing wall? Does it set on top of the trusses running parallel or perpendicular?? Little sketch would be helpful.
As for a fix - nothing easy here, and being a condo, it's a real can of worms. You have my sympathy.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
The interior bearing wall is perpendicular to the trusses. Also, the trusses are mostly spaced 24" o.c. but some are as close as 12" o.c. There are two places where the trusses have been doubled up which I show in the attached diagram.
Then that wall where the deflection is a maximum is acting like a bearing wall, loading the joist, where it was probably originally intentioned to only be a partition wall. The joist is just plainly overstressed. The framing for a partition wall is different than a bearing wall so these kinds of problems do not happen,
You need to get a structural engineer to open up the ceiling over the wall corner and see what's going on, as well as check our the floor framing above. I'm sure you will find more "goodies".
Mike McCann
MMC Engineering
Mike McCann
MMC Engineering
If you add significant dead load to the floor, you will cause more deflection and may overstress the existing trusses. I agree with Mike that you need to consult with a structural engineer to determine the best course of action.
BA
If the trusses were not jacked up to releive the stresses in the truss, then the repair does very little IMHO to fix the truss. If you are trying to sell the place, then you are between a rock and a hard place. You know about the problem so you have to disclose the information to the buyer or get it properly fixed before selling.
If you do not have a copy of the repair than ask for one. If the repair work was not done per the repair drawings, ask them (the HOA and then the contractor) why before/and /or sending the information to the Building Official with your concern about a possible unsafe building condition.
Good Luck.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
I see you are a truss designer, so your opinion regarding the ineffectiveness of the gussets has got me more concerned.
I do have a copy of the repair drawings, but in the instructions the SE left jacking-up the floor to the discretion of the HOA.
Dave
Now I do not have a copy of the original truss design or the repair design to make a comment on. But some engineers would say that a floor truss designed for a 55psf (40psf live, 15psf dead) loading, I am assuming that the trusses were not designed with a partition load. If repaired without any live loads applied the truss would be only (15/55)100%= 27% stressed. So the gussets will be able to start working at 30% stressed. In your case you have a wall that weights, typically, 5psf at 8' high or 40plf for most of the length of the truss. You should look carefully the repair drawing loading to see what loads are accounted for. For a 24" o.c. truss you would have almost (40+2(15))/2(55) or 64% stressed truss at the time of repair. So the repair only starts working at 66%. This is a number game IMHO that I disagree with. I have always required the truss to be jacked up to relieve stresses.
As for adding some type of leveling material, as noted above, the repaired truss may require additional repairs. But the repair design may have added to the loading to account for this or maybe not.
You will have to force the HOA to take action, but you can't legally do it yourself under most condominium provisions.
“Construction Official
The Construction Official receives applications, issues permits, provides inspections, collects fees and answers code enforcement questions for all areas of construction - building, electrical and plumbing.
Contact this office for certificates of occupancy, sign requests, tree removal permits, driveway opening permits, change-in-use permits, developer's fee, and applications for historic appropriateness.
The Construction Official reports information to the Township, County and State, and to the Federal Bureau of the Census. Ken Rogers, Construction Code Official, 212-7000, Ext. 422.
Joe Haggerty, Technical Assistant to the Construction Official 212-7000, Ext. 421.“
Is yours the only unit in the condominium that is having deflection problems? I would have expected other units framed in the same way to be experiencing similar issues. If not, what was different about your floor framing?
Note #10. on each of the three drawings specifies jacking the trusses 1/4" to 1/2" before installing the gussets. If I understand you correctly, that was not done, but in any case, such minimal jacking would not have alleviated a deflection of 1.5".
As Ron has indicated, depending on the condo documents, you probably cannot take remedial action on your own without the permission of the HOA. I do not believe the HOA is entitled to wash their hands of it. They will have to take appropriate measures to provide you with an acceptable floor or face possible legal action.
BA
Mike McCann
MMC Engineering
Regarding legal action, I suppose I could have an attorney write a letter to my HOA, but I think I would need some new, convincing ammunition to get them to take action. Perhaps threatening to go to the township Building Inspector, as Garth Dreger suggested. The plywood gusset work done by the HOA was not covered by a specific building permit. Revealing that information to the township may cause the HOA and contractor to be fined. ??
An attorney told me that going to court would cost me $5,000 just for starters and not including fees of expert witnesses. So, I wonder if I'd be better off devoting the $5,000 towards a fix. At least then I could pick the contractor and control the design.
Whatever fix, or series of fixes happens, it should be agreed to by all parties. Be careful here.
Mike McCann
MMC Engineering
Sorry, I meant would not.
Mike McCann
MMC Engineering
Mike McCann
MMC Engineering
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
You mention only the excessive deflection, which is a "serviceabilty" issue, but there is the even more important "strength" issue of whether the trusses are adequate to support the load without overstress in accordance with the building Code, and if not, do the added gussets bring it into compliance with the Code.
In keeping with that wise engineer's advice, might I suggest that you retain a structural engineer experienced in timber design, to check whether the origional design was correct with regard to both strength and serviceability, and if it was not, then to identify where it was deficient and whether the gussets that were added would fully rectify the problem. If the engineer's report says that it is not deqaute to met Code, then I would expect that the condo corporation would be obliged to fix it properly.
I share the opinions of others about undertaking any repair such as gypsum fill, which I think is unwise unless it is firat checked out by a strcutural engineer. If the trusees have inadequate strength, you will be making things a bit worse, and then you will be liable for any subsequent issues. I don't think that you want to go there.
For a 15 psf dead load (typical) and a 40 psf residential live load, 13 psf is a significant increase.
BA