SKM System Modelling - Separate CPC's (Grounding Conductors)

SKM System Modelling - Separate CPC's (Grounding Conductors)

SKM System Modelling - Separate CPC's (Grounding Conductors)

(OP)
Just a beware

Working with SKM PTW and undertaking fault level and protection studies ?

Working recently with SKM I noticed that the system takes no account whatsoever of separate earth / grounding conductors entered in parallel with the power cables, therefore protection studies and fault level studies involving ground-fault studies are potentially incorrect.

It would appear speaking to SKM that a separate cable entry must be made in the database for each combination of Cable CSA + Ground wire that is to be used ........ either that or unlink the cable from the cable library and manually edit the zero-sequence element of the Z matrix to take into account that parallel conductor.

If you were aware, i apologise for wasting your time ... if you were not, then I hope this has helped ....

Kind regards





RE: SKM System Modelling - Separate CPC's (Grounding Conductors)

cflatters,
If I understand your concern correctly, I think you have to consider those parallel ground paths when you input the
value for the SPLIT fcator.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources