Capacity of a 2x12 joist with a large hole
Capacity of a 2x12 joist with a large hole
(OP)
Can anyone provide a good design example to calculate the shear and moment capacity of a 2x12 joist with a 4" hole drilled 2.25" up from the bottom? I have figured the max shear and moment at that location, but I am not sure how to get a correct capacity. I did calculate an Sx = 24.8 in3, based on conservatively allowing a 2.25" tall "flange" top and bottom like an I-beam (so they would be equal and easier to calculate), but I'm not sure that is correct, nor am I seeing how to properly figure a shear capapcity. It is a continuous joist 8' + 12.5' span, with the hole occuring 4' from the center support into the 12.5' span. Thanks.





RE: Capacity of a 2x12 joist with a large hole
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
RE: Capacity of a 2x12 joist with a large hole
RE: Capacity of a 2x12 joist with a large hole
Grade / Knots at edge / Knots at centerline / Holes any clause / Per lin ft.
#3 / 5.5” / 6.5” / 3.5” / 1'
#2 / 3.75” / 4.75” / 3” / 2'
#1 / 3” / 3.75” / 1.5” / 3'
SS / 2.25” / 3” / 1.25” / 4'
With a 4” dia. hole you have a piece of lumber that can not be regraded as a structural grade.
Per the attached NOTCHING & BORING GUIDE FOR FLOOR JOISTS & STUD WALLS IN CONVENTIONAL LIGHT-FRAME CONSTRUCTION (older guide that was not up dated to the IBC/IRC) from the WWPA at http://www2.wwpa.org/. My attached copy was a free download, now they want $2 to download a NOTCHING AND BORING GUIDE (A-11). So maybe it has been updated to the IBC/IRC.
A 2x12 is allowed a maximum 3.75” hole (minimum of 2” from edge of member) if the joist meet the conventional light-frame construction requirements. Personally I have never agreed with this and have always added a note that no other holes or knots shall be within the above “Per lin. ft.” of the hole.
As your hole is greater than the 3.75” for the conventional light-frame construction requirements or the grading rules sizes. I would replace the 2x12 or add another to it and have them drill an allowable size hole in it if needed. If you decide to “own” the hole. You will need to decide how to calculate it, what CYA notes to use and what personal safety factor to apply.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: Capacity of a 2x12 joist with a large hole
For the shear, I would use the net section.
RE: Capacity of a 2x12 joist with a large hole
On a final note, I found these, http://www.metwood.com/products/reinforcer , which the plumber is choosing to use as a repair. They are $30 each (plus S & H) and come with engineering and an ICC report. They are impressively small with few screws and allow a 6" hole in the center of a 2x10!
RE: Capacity of a 2x12 joist with a large hole
1. The ES Report is under the old BOCA Code, not the IBC or IRC. Might be a problem in certain jurisdictions although it has been updated to 2005. Why the IBC was not mentioned at that time is a concedrn.
2. Make sure the reinforcer is installed before the piping is installed.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
RE: Capacity of a 2x12 joist with a large hole
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: Capacity of a 2x12 joist with a large hole
Many of us, especially in the residential world, use older books to create simpler designs from simpler times, that work. It seems to me that it is not unreasonable to assume that the testing, which is described in the ES report, would still apply to real world applications. I guess it is up to the EOR to decide his level of risk tolerance.
RE: Capacity of a 2x12 joist with a large hole
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.