concrete pad

concrete pad

concrete pad

(OP)
We have a distribution Transformer of 2.8 X 1.5m, we will replace it with a new transformer whose base will need to be 3.3 x3 m. we intend to use the existing pad. is it ok to just put some dowel in it and just extend the existing pad?

RE: concrete pad

It could be, just proceed according to analysis. If your analysis shows you can get reinforcement enough that way for a proper structural behavio
r, it may be a reasonable way to proceed that forfeits demolition works.

RE: concrete pad

I of course would prefer as bridgebuster a new pad, but well, I try to adapt to the surmised intent in the question.

RE: concrete pad

Let me qualify my No. You'll have to analyze the modified footing.

RE: concrete pad

Theoretically, it could work but is it worth the trouble? The labor required to drill holes and the epoxy needed to anchor the new steel is probably worth more than the concrete saved. Demolish the existing pad and build a new pad to the required size.

BA

RE: concrete pad

it is pretty small pad that won't cost you a lot to rebuild.

RE: concrete pad

What is the foundation under the pad, and how thick is it? If the foundation is mass concrete, it should be no problem to just extend the pad. And if the pad is thin (less that 100mm or so), you probably don't need dowels.

RE: concrete pad

Depending on how much of the footing you need to develop to resist overturning, not just bearing, you probably will need the dowels. However, I would STRONGLY recommend to rip and replace here.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: concrete pad

The OP didn't say whether the pad is a footing or a pad on top of an existing concrete floor. We extend equipment pads on top of concrete floors all the time. We just roughen the receiving surfaces and pour the extension. Whether we dowel or reinforce the extension depends on the thickness. If it is a footing - I agree - it should be repoured.

RE: concrete pad

Changes the picture completely. Why not show us this on the first post?

BA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources