1000VAC Motor Fuses

1000VAC Motor Fuses

1000VAC Motor Fuses

(OP)
Is there a fuse not normally seen in North America that would be used on 1000VAC motors? The only options I'm finding are 1000VAC rated semiconductor fuses or the 3" diameter x 10" long, 2400VAC, R-rated motor fuses.

RE: 1000VAC Motor Fuses

I'm not sure - never seen a 1000 V motor, but you might want to call these guys: www.monsterfuses.com

RE: 1000VAC Motor Fuses

Damn, ScottyUK beat me to it.

Older Joy mining machines (and a lot of similar ilk) are 1000V. An ex-employer of mine used to make soft starter controllers for Joy, we used the Siba fuses because there was no room for R type 2400V fuses.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources