Maximum height of concrete masonry walls

Maximum height of concrete masonry walls

Maximum height of concrete masonry walls

(OP)
Is there technically a maximum height limit somewhere? For empirical design there is but for engineered masonry can we go as high as the numbers take us?

For example, a 36 ft. high 8" thick reinforced CMU wall - interior - with only 5 psf on it laterally and no vertical loading except for self-weight.

The numbers work, even taking into account some "extra" out of plane second order effects. But it seems, well, too thin to me.

RE: Maximum height of concrete masonry walls

I have seen an interior 6" stud wall 30' feet high. I am guessing that a masonry wall can go a little higher.

RE: Maximum height of concrete masonry walls

This is from my Standard Handbook for Civil Engineers 3th ed. (1983) section 15-11 Masonry Walls. “Stability... ... Nonbearing masonry partitions should be supported laterally at distances not exceeding 36 times the actual thickness of the partition, including plaster.”
This says it can not be done. But, I would look it a more current Standard before saying that it can not be done.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Maximum height of concrete masonry walls

Canadian code, kh/t for columns <= 30, and walls can be greater... as long as the numbers bear it out.

Dik

RE: Maximum height of concrete masonry walls

ACI 530 has taken out all the good common sense h/30 limits. It's been replaced by practical limits where you just can't reinforce a wall enough over a certain height. I try to stay pretty close to h/30, but have strayed to h/34 or h/36 on occasion. With the LRFD methods it can be done pretty easily.

RE: Maximum height of concrete masonry walls

(OP)
Jed - aren't H/34 or H/36 shorter, tighter limits?

RE: Maximum height of concrete masonry walls

H/30 = 8", H=240"; H/34 = 8", H = 272"; H/36 = 8", H = 288".

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Maximum height of concrete masonry walls

I meant h/t less than 30. I've went to 32 and 34 on occasion.
Garth translated well for me. We Arizona residents need to stick together.

RE: Maximum height of concrete masonry walls

I don't know of any max limits on engineered masonry, as long as the numbers work out. Construction maybe difficult on a wall that tall and slender, but I wouldn't know how to explicitly account for that.

RE: Maximum height of concrete masonry walls

(OP)
Garth - sorry and thanks. Brain fart.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources