DC Resistance difference between phases
Hi everybody,
I tested 180 MVA, YNd1 transformer secondary winding DC resistance as follows,
a-b = 2,5 ohm
b-c = 3,5 ohm
c-a = 2,5 ohm
What can be the reason of this test result? Why "b-c" resistance is different?
Thanks in advance..
a-b = 2,5 ohm
b-c = 3,5 ohm
c-a = 2,5 ohm
Thanks in advance..
RE: DC Resistance difference between phases
No one individually could produce such a difference.
As a general factor we'll take 3.5/2.5=1.4
The result it will be the product of these factors:
1)differ temperature as b-c coil is in midlle of the tank 1.1572[90-55oC]
2)a slight difference in copper diameter4% factor=1.083
3)a slight difference in number of turns 1.04
4) a slight difference in coil diameter 1.05
5) a loose contact resistance 0.02 ohm[could be dangerous!] 1.02
So, it could be something more serious.
#2 Testing resistance on Delta windings requires special considerations to test connections and / or further calculations. Check with you test equipment instruction manual on proper connections.
Check your test equipment!
If you are using a high current test set then be careful when you disconnect the leads: wind the test current down slowly otherwise you will get a large inductive back EMF which may harm your instrument or you.
As to the unbalances, how were these measurements made? Was the delta opened up for each measurement? Or perhaps left connected inadvertently for one or two? Leaving 2R in parallel with R would give you a (false) 2R/3 reading, which is close to what you are seeing.
what are the possibilities of it???
180 MVA GSU Transformer - LV winding in ANSI world would be ~13.8 kV to ~23 kV. I would guess in IEC world ~22kV. Thats a lot of
copper and milli or micro ohms would be expected. The I2R losses at Ohms would burn things (or severely heat) up ~ full load.
This is either a misplaced or mislabeled reading or as PHovnanian mentioned, the 2R/3 calculation was not made, or the test connections are not correct.