B31.3 vs. B31.1
B31.3 vs. B31.1
B31.3 vs. B31.1
The majority of our piping is per B31.3 but on one particular job it is specified as B31.1.  The customer specification also calls for 5% radiography on the butt welds per B31.1.  After reviewing B31.1 it does not appear to specify a % of welds to x-ray if you meet the criteria specified in Table 1 so I assume it is all of the welds meeting this criteria.  The design conditions of this particular job would not require any x-ray in themselves other than the addittional 5% requirement of the customer specification.  The problem is what to do if an x-ray is deemed unacceptable.  B31.3 requires 2 additional x-rays for the rejected one where as B31.1 does not appear to require this (I assume this because the code itself would already require all of the welds x-rayed if you where x-raying based on only the code).  I would assume that the rejected weld needs to be repaired and shot again but do not see any requirement for additional shots.  Not being familiar with B31.1 I was wondering if anyone had any experience with this type of an issue.
RE: B31.3 vs. B31.1
B31.3 Para.341.4 shows examples of NDE using radiography.
Chapter VI in B31.3 will list all inspections but B31.3 will not tell you to what extent you must use as a % of NDE.
 ASME B31.3 is a standard to follow. Most companies require you to follow B31.3 as a minimum requirement.
 If you have shot a weld an it has tested bad the general rule is to repair the weld, then shoot the next three welds the welder makes.
RE: B31.3 vs. B31.1
B31.3 Para. 341.4.1 (1) does say at least 5% of fabrication must be tested with radiography. Some clients may require 10%. It all depends on what the service is. Catagory D may not require any testing other than visual & service test.