REPLACEMENT OF THE EXISTING HVAC PLANT!!!
REPLACEMENT OF THE EXISTING HVAC PLANT!!!
(OP)
Hi Everybody!
I am working on a Offshore & onshore project wherein we need to replace the existing Hvac system with improved Equipment reliability & performance to provide reliable operation..
97 Hvac units(2000 Tons) were serving Substations (2 are onshore), Satellite Instrument house, Analyser room & CCR since 25 yrs..
My question is not how to replace the plant but I am more bothered about the Alternative cooling system...
Before commencing demolition activities the respective buildings shall be provided with stand alone Alternative Cooling by construction contractor for a cooling load equal to the existing capacity to prevent the sensitive electrical and
instrument panels housed inside the buildings from getting damaged.
Proposed Hvac Units & its capacity:
1. Ducted Split A/C - 30T (2Nos)
2. Ducted Split A/C - 9T (4Nos)
3. Ducted Split A/C - 47T (4Nos)
4. Ducted Split A/C - 16T (15Nos)
5. Ducted Split A/C - 14T (3Nos)
6. Ducted Split A/C - 22T (2Nos)
7. Ducted Split A/C - 24T (19Nos)
8. Air Cooled
Chillers - 102T (3Nos)
9. Wall mounted
Package A/C - 5T (14Nos)
10. Bottom Discharge
Package A/C - 8T (14Nos)
(Nominal capacity= 12T)
11. Package A/C - 12.5T (2Nos)
(Nominal capacity= 18T)
Please reflect your experience on this.......
I am working on a Offshore & onshore project wherein we need to replace the existing Hvac system with improved Equipment reliability & performance to provide reliable operation..
97 Hvac units(2000 Tons) were serving Substations (2 are onshore), Satellite Instrument house, Analyser room & CCR since 25 yrs..
My question is not how to replace the plant but I am more bothered about the Alternative cooling system...
Before commencing demolition activities the respective buildings shall be provided with stand alone Alternative Cooling by construction contractor for a cooling load equal to the existing capacity to prevent the sensitive electrical and
instrument panels housed inside the buildings from getting damaged.
Proposed Hvac Units & its capacity:
1. Ducted Split A/C - 30T (2Nos)
2. Ducted Split A/C - 9T (4Nos)
3. Ducted Split A/C - 47T (4Nos)
4. Ducted Split A/C - 16T (15Nos)
5. Ducted Split A/C - 14T (3Nos)
6. Ducted Split A/C - 22T (2Nos)
7. Ducted Split A/C - 24T (19Nos)
8. Air Cooled
Chillers - 102T (3Nos)
9. Wall mounted
Package A/C - 5T (14Nos)
10. Bottom Discharge
Package A/C - 8T (14Nos)
(Nominal capacity= 12T)
11. Package A/C - 12.5T (2Nos)
(Nominal capacity= 18T)
Please reflect your experience on this.......





RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
Install the temporary equipment, which will require some level of demolition, or at least moving stuff around.
Commission temporary equipment.
Remove original equipment.
Install new equipment.
Commission new equipment.
Remove temporary equipment.
Restore anything done to allow installation of the temporary equipment.
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
please help me regarding Alternative cooling...
Thanks....
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
If it is a ductless split, you can probably change out the whole thing in less than a day, so the staging of new and old plant is not so important.
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!
Ductable split A/cs are used in this project.....
i think as you said for sensitive areas we need to provide spot coolers before decommissioning....
As i am a beginner in this field i dont know much about spot coolers or similar equipments. I would appreciate if you share your knowledge about such kind of equipments...Thanx again!
RE: REPLACEMENT OF THE EXISTING HVAC PLANT!!!