I need help regarding BASLER DECS200.
Problem: We are trying to connect to the 13.2KV grid a 3MW SIEMENS-MAN DIESEL Gen-set. The rated voltage of the generator is 13.8KV. Will BASLER DECS200 do the job synchronizing with the 13.2KV grid?
Problem: We are trying to connect to the 13.2KV grid a 3MW SIEMENS-MAN DIESEL Gen-set. The rated voltage of the generator is 13.8KV. Will BASLER DECS200 do the job synchronizing with the 13.2KV grid?





RE: BASLER DECS 200
RE: BASLER DECS 200
Generally there is also a sync check relay (set a little wider for phase angle) as a backup in series with the 25A in the closing circuit.
Both Basler and Woodward make popular units. I'm sure there are others out there as well.
http://www.woodward.com/spma.aspx
http://www.basler.com/html/pcs-synchronizers.htm
RE: BASLER DECS 200
RE: BASLER DECS 200
60 Hertz Sensing
Range 1: 120 Vac (94 to 153 Vac)
Range 2: 240 Vac (187 to 305 Vac)
Range 3: 400 Vac (374 to 600 Vac)
Range 4: 600 Vac (510 to 660 Vac)
Assuming 13.2 kV to 120 V PTs, the unit should work perfectly.
Assuming 138 kV to 120 V PTs the unit will see (13.2/13.8 x 120) 114.8 Volts which is within the sensing range.
Remember this is free advice but it looks as if it will work.
Can you use 13.2 kV:120 V PTs and remove all doubt?
Bill
--------------------
"Why not the best?"
Jimmy Carter