hydro test
hydro test
(OP)
I have a hydro test in which I have to test up against a valve. Problem is the valve is passing and the next valve in the line is a long distance away. Any suggestions?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: hydro test
Remove valve and inspect and if necessary replace.
If the valve cannot hold pressure for the test how is it going to stop product leaking when it is put in service ?
Regards,
Kiwi
RE: hydro test
Regards
Aakash Jha
RE: hydro test