I have a hydro test in which I have to test up against a valve. Problem is the valve is passing and the next valve in the line is a long distance away. Any suggestions?

RE: hydro test

Downhand,
Remove valve and inspect and if necessary replace.
If the valve cannot hold pressure for the test how is it going to stop product leaking when it is put in service ?
Regards,
Kiwi

RE: hydro test

In Addition to Kiwi Comments , you may like to do the seperate testing for valave prior taking any decision that it should be used, reworked & use or Replaced.
Regards
Aakash Jha

RE: hydro test

If the valve is flanged, drop in a 'pancake' hydro test blank. If the valve is welded, try a Freeze Plug just beyond the valve. TEAM is one company that performs Freeze Plugs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources