ATS circuit breaker tripping
The breaker downstream of the ATS trips. It trips when I go from Generator to Utility. It is a fast break before make, 400A, 480V ASCO ATS that transfers in 51-31msec with a current surge on the C phase of 4100A's. The downstream loads are only transformers from the 400A breaker feeding the ATS: (1) 225kVA [271 FLA] (2) 112.5kVA [136 FLA](1) 45kVA [54.2 FLA](1) 30kVA[36.1 FLA]
So, if you take 10x to 12x the FLA of all of them you get 6333A’s-7600A’s inrush for .1 seconds. and my breaker can only go up to 4000A's, but not sure if this surge current is from that or from the fast transition - help in understanding this is appreciated.
The transfer switch I believe allows a larger transfer time of 1 second - would that help? Would it help if the generator had more load on it? This is the last switch out of 12 to transfer. Is this current surge from the fast transition time or is it from the inrush to the transformers (asked already)? I might be able to install a time delay between the largest transformer via a large contactor with a timer.
The obvious solution would be to increase the breaker frame size to accomadate this surge (unfortunatly I inherited this mess and the engineer before me assured them this would work
. A closed transition ATS would also work, but would have to evaluate fault currents for downstream equipment. Any other solutions.
RE: ATS circuit breaker tripping
It does have an in phase monitor and I am going to double check the settings and put it at 5 degrees at 1.5 seconds - thoughts? The in phase monitor should really eliminate the high surge currents correct?
Bill
"Why not the best?"
Jimmy Carter