Hello,

Could someone explain what the minimum voltage rating means on a circuit breaker. The breaker is a Square D Type FG2 with the following nameplate information:
Continuous Current 1200 Amps
Minimum Voltage 13.8 kV (although manual lists this as 11.5 kV with 13.8 kV as a nominal voltage)
Maximum Voltage 15.0 kV

My concern is that this breaker is used in an application where the voltage is 6.6 kV. I can understand a maximum rating but why a minimum voltage rating?

Thanks in advance to all replys.

RE: Breaker nameplate minimum voltage

I've only seen this used for a "constant MVA" approach to short circuit rating. This approach was dropped a while ago. Basically, the symmetrical interrupting capability of a breaker was increased as the voltage was decreased (hence constant MVA) down to the minimum voltage. Below the minimum voltage, the interrupting rating stayed the same.
Like I said, this approach was dropped a while ago. Functionally, the breaker will operate the same at 6.6KV, you shouldn't have any issues.

RE: Breaker nameplate minimum voltage

wbd,
Previously ANSI bkrs were classified as "constant MVA" and therefore "Voltage Range factor (K)" was defined.Your bkr must have K=1.30 printed on the name plate.That
means it can operate from 11.5 kV to 15.0 kV range. Accordingly the rated sym. interrupting capability varies from 23 kA to 18 kA.Now, ANSI C37.06 is harmonized with
IEC 60056, therefore now K=1.0.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources