Hi All,

I have a NYB vane axial fan with a 25 HP motor on a pulley and it draws about 18 HP running load. On startup the fan screeches very very loudly. A pulley alignment check was made by the fan contractor and supposedly everything is okay. The belt is tight. The belt supposedly shows powdery wear on all sides of the belt. The fan aligment contractor advises the motor has too much torque capability and the belt is slipping on startup. He advises to put on a vfd to get a softer start. Something that he is saying is not right. Any comments? Thanks

RE: Fan Screeching Noise

Or change to multiple belt pulleys.

RE: Fan Screeching Noise

(OP)
From what i remember there are 4 or 5 belts already. Supposedly the belts match the pulley

RE: Fan Screeching Noise

Quality Time.
Check that the belts themselves are a matched set, there will usually be code numbers on the belt.
If somebody has changed a worn belt with an odball, they may not be tensioning evenly, allowing one or two belts to slip.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor

RE: Fan Screeching Noise

How big is the fan? Large diameter low speed fans accelerate slowly, and the motor wants to be at nominal speed almost immediately. During acceleration the motor can deliver 2x - 3x nominal torque, assuming it's a standard induction motor so it is possible that the belts are slipping during acceleration. Of course any competent designer would know this and make allowances in the belt drive for the acceleration torque... so what your contractor is saying may have a grain of truth, but a soft start or VFD sounds like it is patching a weak design.

RE: Fan Screeching Noise

Increase both pulley diameters - keeping the ratio the same. That will reduce belt tension for the same torque.

RE: Fan Screeching Noise

(OP)
I was on a scissor lift today to look at it first hand with a millwright. A spirit level was used and the belt was inspected and it is consistent with it not being aligned even though the contractor said it was aligned. Thanks everyone.

RE: Fan Screeching Noise

Check sheave wear while you're at it. Sheave grooves should be v-shaped, not dished.

Also consider going with cogged belts unless you are already using them.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources