Contactors
Contactors
Contactors
Hi Guys
I recently started working on an oil rig and we seem to be having some problems with the anchor winch contactors. As the rig is 40 yrs old the system is obsolete and attempts at finding spares have been futile. I want to know whether its possible to just replace the contacts or coils of the contactors. Replacing the entire system is not an option at this point.
RE: Contactors
Contacts and coils may or may not be available. But it will be faster to replace the entire contactor. I don't understand why that is not an option, if you think you will be able to replace the contacts and coils.
RE: Contactors
Buy a new complete contactor. Install it where you have space. Run the power and motor conductors to the new contactor location. We can't help you with spare parts. Even if spares parts are available we would need the make and possibly the size or model number.
Bill
"Why not the best?"
Jimmy Carter
RE: Contactors
As a general rule, a 40 year old contactor has most likely outlived it's usable lifespan. Winches are considered Inching / Plugging duty, so figure the electrical lifespan is 60,000 operations (unless it was de-rated at design time). That is 10 operations per day for 16 years. The mechanical lifespan on a larger contactor (you don't say the size) is likely 5,000,000 operations which is longer, but it's unlikely that replacement contacts are even available for something that old. There are companies that will fabricate contacts for old obsolete contactors, but look at the cost vs benefits first. If the contactor has been abused or neglected, your mechanical life may be seriously compromised and you could be throwing good money after bad. I would just replace it with another PROPERLY SELECTED modern contactor.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)