INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Appendix D

Appendix D

Appendix D

(OP)
Anyone know of any good computer programs that handle the requirements of anchor bolt design in accordance with Appendix D of the IBC or OSSC?

Not Hilti where the bolts are afterset, but cast-in-place situations only.

Thanks in advance.

Plans checker is demanding an Appendix D analysis even though seismic does not control by a longshot, which is unreasonable, but we still have to deal with it, whatever "it" is.... :)

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Appendix D

Tension = 0#, Shear = 0#, Anchor ok (per ACI 318-08 section D.2.1) by inspection?

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Appendix D

Hilti Profis, as well as the Simpson equivalent, provide calculations for cast-in-place anchors. They both do headed anchor rods and headed studs, while only Simpson's will check L- (aka J-) and U-bolts. As for ease of use and presentation of output, Hilti's wins hands down.

RE: Appendix D

We also use Powers fastener's program.

RE: Appendix D

It doesn't sound like it will matter to you but Appendix D is based on un-reinforced concrete and is overly conservative for piers or near slab edges where you have provided secondary reinforcement. Appendix D provides only minimal credit via a static coefficient for "supplemental" reinforcement.

RE: Appendix D

The current versions of Appendix D allow pretty much full credit for bars that properly develop into your breakout cone and then back into base concrete, so it's not that difficult to do things like pedestals anymore. In the first version, it was difficult proving that you'd followed the code in those situations, as it wasn't clearly explained.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources