We are getting megger test resulst back on new lightning arresters with the follwoing values:

Phase A - 6,000 megohms
Phase B - 56,000 megohms
Phase C - 7,000 megohms

Any reason to be concerned about on the large discrpeancy in Phase B or possible causes?

Thanks.

RE: Megger test results

What type of arrestor do you have...(Gap type?)
If so possibly due to incorrect gap size, corrosion, poor connection somewhere in circuit?
Does manufacturer give installation/commissioning details.

rolmag175

RE: Megger test results

Phase to ground results, not phase to phase, correct?

What are specifications for each? (High resistance, or low?)

RE: Megger test results

(OP)
I would have to verify what type of arresters we have. Yes, the values are phase to ground.

RE: Megger test results

Are you meggering them the same way (positive or negative to ground)each time?
At what voltage are you testing?
What voltage are the arrestors rated for?

RE: Megger test results

Presumably this is an MOV type arrestor as this is an LV installation, judging from you using a megger rather than anything more sophisticated. If your megger test voltage is right up near the kneepoint of the arrestor then some leakage is quite likely. The V/I characteristic at the kneepoint is anything but linear, so manufacturing tolerances in the arrestor could easily explain the difference you are seeing.

Moral: don't do megger tests with MOVs on the system because the results are often confusing. wink

RE: Megger test results

(OP)
yup, MOV type of arrestor.

Called manufacturer. They stated that the phase B arrestor may be a different voltage rating (10kV vs 12kV) which may be causing the big swing. That doesn't make sense to me.

Still not sure if the big swing in megohm on phase b is a concern. I am having retesting perforomed to see if this was a typo or operator error.

Thanks.
b

RE: Megger test results

The readings appear to be acceptable in accordance with NETA ATS-2009. I'll reiterate what others are saying: Check with the manufacturer, verify that the 'B' phase arrestor is the same as the others, retest.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources