Column Base Grouting
(OP)
Is there any method or material appropriate for restablishing bearing under column baseplates that have a slight gap under them due to either unlevel leving plates or tilted column bases that resulted after leveling up the erected steelwork?
I am referring to tapered gaps in the 1/8" to 1/4" dimension.
An initial search seems to indicate that grouts need to be 1" or greater in thickness.
I am referring to tapered gaps in the 1/8" to 1/4" dimension.
An initial search seems to indicate that grouts need to be 1" or greater in thickness.






RE: Column Base Grouting
RE: Column Base Grouting
Non-tapered shims would only make very small contact and would basically mirror the condition at the other edge having contact.
RE: Column Base Grouting
And I think the statement is saying that if the reduced bearing area is sufficient to carry the load, you don't need to do anything, but if you need something, it says add non-tapered shims. They get this from testing they did, per the commentary.
RE: Column Base Grouting
Is the reason for the generic 1" to 2" grout the realization that a very thin, tapered 1/8 or 1/4" grout filler simply can't be injected under a baseplate sufficiently even enough to ensure enough face-to-face contact on both top (grout-to-baseplate surface) and bottom (grout-to-concrete surface) of the grout?