We were 10 days into a 14 day flush prior to occupancy.
I discovered the breakers to the outdoor air source had been inadvertently turned off for an inspection of the fire alarm relay and not turned back on. Breakers were off for 3 days before anyone noticed.
Is the flush requirement continuous?
If so can we now change to flush before occupancy?
thanks,
tab
I discovered the breakers to the outdoor air source had been inadvertently turned off for an inspection of the fire alarm relay and not turned back on. Breakers were off for 3 days before anyone noticed.
Is the flush requirement continuous?
If so can we now change to flush before occupancy?
thanks,
tab





RE: LEED EQ 3.2 Building Flush
You should be able to document that the overall space has maintained greater than 60°F and less than 60 %RH while the necessary OA was delivered. It's easy to achieve this if heating is available and space temperatures are set very high (override space set points to 78°F for example).
RE: LEED EQ 3.2 Building Flush
RE: LEED EQ 3.2 Building Flush
As per the work programme you still can continue during the occupancy period as stated by chasebean1 under his discussion.
Have you had a Indoor quality management during constrction phase?
H-VAC
RE: LEED EQ 3.2 Building Flush
And we did have a IAQ plan during construction which included photos of the various dust control measures.
All is documented and included on a trend from BAS.
Thanks to all,
Tom